We are attempting to use a Digi One IAP as a convertor from Modbus on RS485 to Modbus TCP.
I have on here locally and it works exactly as I would expect. I can wire up the Terminal block using pins 3,4,5 or 5,6,7 and in both cases it works perfectly.
Or QA (located in another country) has a Digi One IAP, and I attempted to help them set it up exactly the same way. Same configuration, wiring and DipSwitch positions.
Ultimately we isolated the issue to that their Digi One, when in RS485 Half Duplex 2Wire mode is not joining Pins 3&6 and 4&7 internally.
We were able to get them running by manually joining the pins externally.
My Digi One is a few years (~5 I think) older and the one down there is fairly new.
Has something changed on the hardware?
What else could we be missing?
Thanks!