Modbus response for first N7 register places CSP header data (Value 0x42) into the response 2nd byte.
Scanning PLC-5 register N7:2.
Modbus scan register is 2.
N7:2 value is x50 (decimal 80).
N7:4 value is x20 (decimal 32).
Response to Modbus poll: 01.03.00.02.00.01.25.CA.
is: 01.03.02.50.42.04.75.
Response to poll:01.03.00.02.00.02.65.CB.
is: 01.03.04.50.42.20.00.52.E7.
ia target is plc5.
Should this be fixed in the ia table for the abethernet protocol or in the serial section?
Make sure you use the latest firmware, which is the G2. Digi doesn’t own a PLC5, so support for that command-set has always been (per the Readme file) limited to how a ControlLogix likes the PLC5 requests formed. However, for firmware G2 a large customer worked to confirm the PLC5 support. I forget the details, but there was some off-by-one issue fixed related to how the PLC5 response (which was a different form than how the CLgx replied) was parsed.